Reseting a BACnet b4920 back to the factory default IP address

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Reseting a BACnet b4920 back to the factory default IP address
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • ScottLeedberg
    ScottLeedberg
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4324 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Reseting a BACnet b4920 back to the factory default IP address

Picard Product_Support
‎2018-09-07 12:39 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-05-19 04:12 AM

Issue

How can a BACnet b4920 be reset back to its factory default IP address?

Product Line

Andover Continuum

Environment

BACnet b4920

Cause

There is no Reset IP switch on the b4920

Resolution

There are 2 ways of accomplishing this.

 

Method One - The first method resets the controller to factory default address settings:

IP Address: 169.254.1.1
Subnet Mask: 255.255.0.0
Gateway: 0.0.0.0
Webserver Port: 80
Web User Name: acc
Web User pwd: acc
EnergyNet ID: 1
BacNetMstpNetId: 2764
BacNetUDPNetId: 2765

During controller startup, there is a 2 minute window in which the controller will be restored to factory defaults based on the following:

  1. Seconds since startup is < 120
  2. A Ping packet is received by the controller with a matching Ethernet address but unmatched IP address.
  3. Ping payload size of 255 bytes.

Prior to running the procedure, the controller must be on the same network as the PC that that is used to issue commands.  The engineer will need to have on hand (1) IP address that is both valid and NOT in use on the network that the PC and Controller are connected to.

 

  1. Get the Controller's MAC Address
    Each controller has a 6 byte hardware address, also known as the MAC address or Ethernet address. The address is represented in HEX. The first three bytes of the MAC address are constant and represent Andover Controls vendor ID : 00-40-11
    The last 3 bytes of the MAC address are derived from your controller’s serial number. The controller’s serial number is printed on the board and is represented as an Integer value. You must convert this value to HEX in order to obtain the last 3 bytes of your controllers MAC address.
    Ex. Integer Serial Number: 1033394
    Converted to Hex: FC4B2
    Controller’s MAC: 00-40-11-0F-C4-B2
     
  2. Create a batch file
    Create a batch file named Acc.bat with the following content:
    arp -s %1 %2
    ping -l %3 %1
    arp -d %1
     
  3. Restart the b4920 Controller
    Within 2 Minutes of restarting, run the batch file with the 3 arguments:
    Acc.bat IP_Address 00-40-11-XX-XX-XX 255
    Where IP_Address = valid IP on the network
    Where XX-XX-XX = last 3 bytes of controller’s MAC
    Where 255 = Ping Payload size
     
  4. After Issuing the command, the controller should restart, and the factory default address settings are restored. 

 

Method Two - Capture the Controllers Currently Configured IP Address

This second method is easier to do and is currently recommended because of its ease.

  1. Download and install a network sniffing application, such as Wireshark which can be downloaded from their website here.
  2. Connect a Cross over Ethernet cable between the b4920 and a PC running the network sniffing application.
  3. Start up the network sniffing application and then reset the b4920 by hitting the reset button on the controller.

On start up, the controller will send out the IP address (Gratuitous ARP Packet) which it currently has assigned to it.  Once this IP address is captured with Wireshark etc the IP of the Workstation can then be changed to allow connection to the controller's web configuration page to change its IP address as required.
 

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 2578
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore