Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Repair LacNet (Xenta programmable) communication in a Xenta 5/7/9xx

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Repair LacNet (Xenta programmable) communication in a Xenta 5/7/9xx
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1844 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Repair LacNet (Xenta programmable) communication in a Xenta 5/7/9xx

Picard Product_Support
‎2018-09-09 09:21 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 04:56 PM

Issue

See Check Xenta programmable online status from a Xenta 5/7/9xx LON node to determine if the Xenta 5/7/9xx controller is communicating with Xenta programmable controllers on the network. If it's not, graphic pages in certain Xenta units won't display data, or connection objects won't pass data as expected, etc.

Product Line

TAC Vista

Environment

  • Xenta Server
  • Xenta 511, 527, 701, 711, 721, 731, 913
  • LNS Database
  • XBuilder

Cause

A Xenta 5/7/9xx LON node pulls "double duty" as both a LON device and a Xenta device. It requires one Xenta Group Binding on message tag 0 to facilitate communication with Xenta programmable controllers.

Resolution

  1. Check LacNet status (see Check Xenta programmable online status from a Xenta 5/7/9xx LON node).  If controllers are showing an offline status, proceed with the following steps.
  2. In LonMaker, right-click on the device and go to Properties. View the address table.
  3. The Xenta 5/7/9xx controller's address table should have the first entry (message tag 0) populated with an index that matches all the Xenta programmable controllers on the network (see Verifying Xenta Group Bindings in an LNS system for more information about checking address table group bindings).
  4. If the group binding for LacNet communication doesn't exist or is wrong, redo group bindings.
  5. Ensure the Xenta group masters of the network have not been manually removed from the network pane of the XBuilder project.
  6. Download the XBuilder project to the device.
  7. Recommission the device in LonMaker.
  8. If it is still not communicating, download each of the Xenta units that it is trying to communicate with and recommission them in LonMaker.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5222
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of