Remote Alarm Manager – Including Date and Time in Alarm Messages

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Remote Alarm Manager – Including Date and Time in Alarm Messages
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • sesa125819
    sesa125819

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1208 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Remote Alarm Manager – Including Date and Time in Alarm Messages

Picard Product_Support
‎2018-09-07 11:37 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-20 05:25 PM

Issue

Alarm messages generated by the Remote Alarm Manager (RAM) do not include the date and time by default. However, some sites require this information to be present in the alarm text messages for compliance or operational clarity.

Product Line

Satchwell BAS & Sigma

Environment

Remote Alarm Manager

Cause

By default, RAM's basic text message configuration does not include the alarm date and time. This omission may not meet specific site or regulatory requirements for timestamped alarm notifications.

Resolution

To include the date and time in the alarm message, follow these steps to modify the message script in the RAM Console:

  1. Open RAM Console.
  2. Navigate to Configuration and select the required Action.
  3. Click Edit on the selected Action, then go to the Messages tab.
  4. Select the Advanced option and click Edit Script.
  5. In the Script Editor:
    • Go to File > Open File.
    • Browse to and open the desired script file.
  6. Modify the script to include the required fields.

Example Script Output Format

For Alarm Messages:

Message No (non-configurable), Alarm Priority, Alarm Date/Time, Mnemonic, Value (e.g., Plant On / Plant Off)

For Alarm Cleared Messages:

Message No (non-configurable), Alarm Date/Time, Mnemonic, Value (e.g., Plant On / Plant Off)

💡 Tip: An example script file is available for download: [RAM Script.zip]

Labels (3)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
Attachments
RAM Script.zip
Tags (2)
  • Find more articles tagged with:
  • 5109
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore