Remote Alarm Manager 2.0 - RAM is unable to read the Sigma alarm record file.
  • Remote Alarm Manager 2.0 - RAM is unable to read the Sigma alarm record file.
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-06 01:06 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-21 11:31 PM
Remote Alarm Manager (RAM) 2.0 is unable to read the Sigma alarm record file.
Satchwell BAS & Sigma
  • Satchwell Sigma
Corruption has occurred in the files stored in the Runtime Folder used by RAM.
To resolve the issue, follow these steps:
  1. Stop the RAM Services
    • Open the Services window and stop the Remote Alarm Manager service.
    • Alternatively, initiate a change in the RAM Computer Configuration. When prompted to stop services, select Yes.
  2. Locate the Runtime Folder
    • The location of the folder may vary depending on the operating system and installation path.
    • Use the Search function in Windows to locate the folder named Runtime.
  3. Delete Contents of the Runtime Folder
    • Navigate to the Runtime Folder.
    • Delete all files inside the folder, but do not delete the folder itself.
  4. Restart RAM Services
    • Return to the Services window and restart the Remote Alarm Manager service.
    • Verify that RAM is now able to read the Sigma alarm record file correctly.
  • Satchwell BAS & Sigma
Tags (2)
  • 6525
  • CraigEllis25