Read unsigned 8-bit (byte) values from a Modbus holding register and represent the analog value in EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Read unsigned 8-bit (byte) values from a Modbus holding register and represent the analog value in EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4618 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Read unsigned 8-bit (byte) values from a Modbus holding register and represent the analog value in EBO

Picard Product_Support
‎2018-09-11 07:28 AM

Last Updated: Picard RobertAndriolo Picard ‎2022-08-18 06:56 PM

Issue

How do I read unsigned 8-bit (byte) values from a Modbus holding register and represent the analog value in Building Operation?

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled

Cause

In this case, the Modbus holding register is a 16-bit unsigned value that is used by the Modbus device to represent two individual 8-bit values.  The 16-bit unsigned value is an integer with a range of 0 to 65,535 and needs to be converted into two analog values.

Resolution

Use a Building Operation Modbus Analog Input Point for each value required.  Each object will be configured to read the same Modbus register address with the bitmask value applied before evaluating the value to determine the output.

For example: Read Modbus holding register 40001 which is a 16-bit unsigned value and decode as two analog values.

Under the Modbus device object - create a Modbus Register Group
Under the Modbus Register Group - create two Modbus Analog Input Points

Configure each point as follows:

  • Modbus Analog Input Point 40001 (AI-HighByte)
    • Register number 1
    • Register type 16-bit unsigned
    • Read function code 03
    • Bitmask - enable all bits 8 through 15
  • Modbus Digital Input Point 40001 (AI-LowByte)
    • Register number 1
    • Register type 16-bit unsigned
    • Read function code 03
    • Bitmask - enable all bits 0 through 7

Additional information can be found in the Building Operation Technical Reference Guide - Modbus Point Configuration (Bitmask) or WebHelp at Point and Value Configuration

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 15999
  • MahmoudSayed22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore