RP-C Modbus Usage with 64-Bit Registers and Multiple Ports
Select a Country
  • RP-C Modbus Usage with 64-Bit Registers and Multiple Ports
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
PeterLarsen Champion
‎2023-12-07 02:11 PM
Last Updated: CraigEl Champion ‎2023-12-10 06:24 PM
  1. How are Modbus 64-bit registers calculated in the Modbus limitations on an RP-C?
  2. Can both RS485 ports be used for Modbus on an RP-C?
  • SpaceLogic RP Controller series
  • RP-C Modbus
  1. EBO version 2023 introduced 64-bit register support in RP controllers. EBO Webhelp states that an RP-C has a maximum limit of 250 Modbus registers. It is unclear if a 64-bit register is counted as four 16-bit registers or just one register on the Modbus maximum count.
  2. The RP-C controller has two RS-485 ports, and it is unclear if both ports can be utilized for Modbus simultaneously.
  1. A 64-bit Modbus register is counted as one register in the Modbus maximum register count.
  2. The RP-C controller has two configurable RS-485 ports that can be used for:
    • Sensor bus
    • Room bus
    • Modbus network
    As per EBO webhelp, the controller can host two networks, but only one network of each network type.
  • PeterLarsen23