Questions on Sigma backup NiMH batteries.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Questions on Sigma backup NiMH batteries.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1147 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Questions on Sigma backup NiMH batteries.

Picard Product_Support
‎2018-09-06 09:52 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-20 11:38 PM

Issue

This article addresses common questions regarding the NiMH battery packs used in Sigma X96 controllers, including:

  1. What is the average shelf life of these batteries?
  2. Can the battery voltage be checked without disconnecting them from the controller?
  3. Is there a recommended preventative maintenance interval for checking the batteries?

Product Line

Satchwell BAS & Sigma

Environment

Sigma UNC controllers

Cause

These questions typically arise during routine maintenance or troubleshooting of Sigma controllers, especially when assessing battery health or planning replacements.

Resolution

 

  • Battery Shelf Life

    • NiMH cells degrade over time, especially in long-term storage.
    • Typical shelf life: Up to 2 years.
    • Risk: Prolonged storage can lead to internal short circuits, a known characteristic of NiMH chemistry.
  • Measuring Battery Voltage

    • Direct measurement without disconnection is not recommended.
    • If the battery remains connected, the voltage reading will reflect the charge circuit, not the battery itself.
    • Recommended method:
      • Power down the controller completely (turn off both mains and battery switches).
      • Insert multimeter probes into the back of the battery connector to measure voltage.
    • Note: Voltage alone is not a reliable indicator of battery health.
      • For accurate assessment, measure the run-time on battery power or use a commercial battery analyzer.
  • Preventative Maintenance Interval

    • No fixed interval is officially specified.
    • Why? Battery lifespan is influenced by several factors, especially ambient temperature.
    • Best practice: Monitor battery performance periodically and replace if degradation is observed.

 

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 15004
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore