Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Purpose behind TAC dummy nodes

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Purpose behind TAC dummy nodes
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1551 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Purpose behind TAC dummy nodes

Picard Product_Support
‎2018-09-10 06:08 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:02 PM

Issue

The reason for TAC dummy nodes and the logic behind the number of dummy nodes created.

Product Line

TAC Vista

Environment

  • Vista
  • NL220
  • LonMaker
  • TAC Vista System Plug-In

Cause

TAC dummy nodes are added to Xenta groups automatically in the LNS network. The dummies are made after group bindings have been created.

Resolution

The TAC dummy nodes are created when group bindings are made. For more information about group bindings see Verifying Xenta Group Bindings in an LNS system.

Vista requires that the TAC Group and the TAC Xenta group differ in the number of devices. If you only have one Xenta group in your system, TAC Vista System Plug-In will create a dummy device and use its tag_0 (also first row of the address table) in the group binding for the TAC Group. This will allow Vista to differentiate between the TAC and Xenta groups. Notice that in both LonMaker and NL220, this dummy node that is created to represent a second Xenta group appears to be located in the same Xenta Group as the rest of the controllers. This is fine, the system plug-in is not going to create a new group to put it in, just realize why the dummy node is there. Modules do not count in the group bindings therefore the example below only has three devices in Xenta group 1.

 

Xenta Groups must consist of at least three Xenta devices. If you only have two Xentas in a Xenta group, TAC Vista System Plug-In will also use a dummy device, since a binding between just two devices is not considered a group binding. To create a group binding, a third device is needed. Consequently, you will need two dummy devices if you only have one Xenta in your Xenta group. Thus, if just one Xenta device exists in a single Xenta group, three dummy devices will be needed: one to separate the TAC group binding from the Xenta group binding and two more to form a Xenta group.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7193
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of