Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Programming a 7798C controller with a Virtual HHC Console

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Programming a 7798C controller with a Virtual HHC Console
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Derrick_Ratliff
    Derrick_Ratliff
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2928 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Programming a 7798C controller with a Virtual HHC Console

Picard Product_Support
‎2018-09-06 02:45 PM

Issue

Programming a 7798C controller with a Virtual HHC Console

Environment

  • 7789C
  • HHC Hand Held Console

Cause

The 7798C controller can only be programmed with the Emulated HHC Console (The TacHHC.exe is located in the support folder of the INET install CD) using CBL 082 connected to the PC and RS 232 port on the controller.

Resolution

Before following these steps, make sure you have closed down I/NET, AMT and the InetIOServer applications.   

  1. Locate the HHC file on the I/Net CD, Support Folder and copy it to the Root of I/NET.
  2. Once copied, double click on the file to launch it, I/NET should not be running at this time.
  3. Connect the CBL 082 (Grey shroud connects to the PC) 
  4. The virtual HHC is displayed at this time.
  5. Right Click and Select the Com Port and Baud Rate.

To Set the Controller Type:

  1. On the HHC, select Code 90, Enter to set the Controller Type.

To Set the Controller Address

  1. Select "DCU Address"
  2. Enter he desired Address

To Set the Baud Rate

  1. Code 06 for C-LAN
  2. Code 91 for Sub-LAN baud rate.

To Direct Connect

  1. Once completed, disconnect the CBL 082 from the PC and replace it with CBL 072 for a direct connect to the controller.
  2. Start I/NET and open the configuration editor, create a new profile for a direct connect, if it has not been created already.
  3. Make this configuration active, close the configuration editor down as well as I/Net, and then restart it again.
  4. At this time communications should be established with the controller and the user can start programming the controller. 
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 3138
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore