Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Problem with Override control of BACnet Output objects within StruxureWare Building Operation on IA Series Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Problem with Override control of BACnet Output objects within StruxureWare Building Operation on IA Series Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2175 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Problem with Override control of BACnet Output objects within StruxureWare Building Operation on IA Series Controllers

Picard Product_Support
‎2018-09-10 01:16 PM

Last Updated: Guinan RandyDavis Guinan ‎2021-11-04 12:27 PM

Issue

  • Problem with Override control of BACnet Binary Output (BO) on IA Series BACnet Unitary, VAV and Zone controllers with firmware version 1.420 or earlier. When a BO override is released the value will not reflect the correct null state and may appear to still be in the previous state.
  • After relinquishing the priority from the point, the actual Priority status shows up correctly as "Null". However, this is not reflected in the Building Operation Workstation "Watch" window.
    (Click on image below for larger view)

Product Line

TAC IA Series, EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation 1.2
  • Automation Server
  • BACnet Interface with MNB 1000 with MNB 300, MNB-Vx, or MNB-70.

Cause

When requesting the complete "Priority Array" for an output object, the values returned match their actual values, i.e. 0, 1 or "null". When requesting individual "priority array indexes" index numbers that are "null" will incorrectly return a 0 or a 1.

Resolution

MNB series V1.424 firmware for the VAV, Unitary, and Zone controllers resolves this issue. When an individual "priority array index" is requested, the priority input value of 0, 1, or “null” is returned. The issue only applies to the MNB-V1, MNB-V2, MNB-70, and MNB-300. The MNB-1000 does not have the "Priority Array" problem.

The MNB series V1.424 firmware files are placed in the WorkPlace Tech firmware folder during the installation of WorkPlace Tech 5.8.2.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Attachments
Tags (2)
  • Find more articles tagged with:
  • 11330
  • RandyDavis21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of