Issue
The appropriate jar files have been installed in the host computer and in the UNC-520's remote library. For more information see Lon jar files required to integrate a Proview display into a Niagara R2 UNC.
The shadow object for ProView successfully pasted to the Workspace. Right-clicking on the shadow object and selecting the wizard generates a pop-up error indicating a missing resource file.
Product Line
TAC IA Series
Environment
- Niagara R2
- ProView
Cause
The host computer has never been used previously to configure ProView and the installer program was not performed.
The lonworks bin directory is missing the executable named DRFupdate.exe. Also, there are other support files that should exist in this directory.
Resolution
Run the installer executable file which comes with the ProView zip package on the host computer. The ProView zip package can be downloaded from The Exchange Download Center.