Planning for Continuum LAN Upgrade

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Planning for Continuum LAN Upgrade
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • GavinHe
    GavinHe

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2223 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Planning for Continuum LAN Upgrade

Picard Product_Support
‎2018-09-07 12:24 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 03:40 PM

Issue

There is a lack of clarity regarding the necessary preparation steps for upgrading a Continuum LAN system. Inadequate planning can lead to compatibility issues, data loss, or system downtime.

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • SQL Server

Cause

Upgrades without proper preparation may result in:

  • Software and hardware incompatibility
  • Data integrity risks
  • Extended system outages

Resolution

To ensure a successful upgrade, follow these best practices:

1. Review Compatibility Matrices

  • Consult the Continuum Compatibility Matrix and Continuum Video Compatibility Matrix.
  • Use these tools to plan upgrades for all supporting software and hardware.

2. Verify Software Compatibility

  • Ensure that .NET and SQL Server versions are compatible with the target Continuum version before starting the upgrade.

3. Update Controller Firmware

  • Older CX controllers (firmware ≤ 1.500029) use a different handle algorithm and must be upgraded prior to the LAN upgrade.
  • Other controllers can be upgraded after the front-end systems are updated.

4. Assess Hardware Requirements

  • Evaluate all current computer hardware, especially the Continuum Database Server.
  • Choose hardware based on customer needs and system requirements.
  • This decision should involve engineering expertise and likely the customer’s IT department.

5. Consider Off-Site Preparation

  • When deploying a new database server, it may be beneficial to build and prepare the Continuum server and database off-site.

6. Engage Experienced Engineers

  • The upgrade process is complex and should be led by an engineer experienced in Continuum LAN upgrades.
  • This ensures proper execution and provides mentorship for technicians involved in future upgrades.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4477
  • GavinHeward25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore