Persistent Routing on the Sigma Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Persistent Routing on the Sigma Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2669 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Persistent Routing on the Sigma Server

Picard Product_Support
‎2018-09-06 02:42 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 08:50 PM

Issue

Guidance on how to add a persistent route to a Sigma server PC connected to a flat Ethernet network, particularly when RIP (Routing Information Protocol) cannot be used on DNNs.

Product Line

Satchwell BAS & Sigma

Environment

Satchwell Sigma Server

Cause

In environments where the Sigma server communicates via Ethernet or Arcnet through DNNs, and RIP cannot be run, manual configuration of persistent routes is required to ensure reliable communication.

Resolution

Understanding Routes

A route in networking defines how data packets travel from one device to another across networks. Each device maintains a routing table, which acts like a GPS for network traffic—guiding packets to their destination based on IP addresses.

  • Static Route: A manually defined path that doesn’t change unless updated.
  • Persistent Route: A static route that remains active even after a reboot (enabled using the -P flag).
  • Default Gateway: A fallback route used when no specific route matches the destination.

In the Sigma environment, adding persistent routes manually imay be necessary to ensure the server knows how to reach each DNN subnet.


Network Example

A flat Ethernet network has no subnets.
Example:

  • Network Address: 10.158.0.0
  • Subnet Mask: 255.255.0.0
  • Valid IP Range: 10.158.0.1 to 10.158.255.254

Adding a Persistent Route

  1. Open Command Prompt:

    • Click Start
    • Select Run
    • Type CMD and press Enter
  2. Use the ROUTE ADD Command:

    ROUTE ADD -P <Subnet Address> MASK <Subnet Mask> <DNN Ethernet IP Address>
    

    Example:

    • DNN Subnet: 192.168.1.0
    • Subnet Mask: 255.255.255.0
    • DNN Ethernet IP: 10.158.1.6

    Command:

    ROUTE ADD -P 192.168.1.0 MASK 255.255.255.0 10.158.1.6
    

    This tells the Sigma server:
    “To reach any device in the 192.168.1.x range, send traffic to 10.158.1.6.”

  3. Verify the Route:

    • Type ROUTE PRINT at the command prompt
    • Confirm the route appears at the bottom of the list
  4. Repeat for Each DNN:

    • Add a separate route for each DNN in the network

Additional Notes

  • This configuration ensures persistent routing even after system reboots.
  • It’s essential in systems where dynamic routing protocols like RIP are not feasible or supported.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 3274
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore