Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

PM5340 does not update values via BACnet in EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PM5340 does not update values via BACnet in EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1792 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PM5340 does not update values via BACnet in EBO

Administrator CraigEl Administrator
‎2023-05-30 05:51 PM

on ‎2023-05-30 05:51 PM

Issue

Values in EBO from a PM5000 series energy meter do not update

Product Line

EcoStruxure Building Operation, Field Devices

Environment

  • Building Operation Server
  • BACnet
  • PM5000 series energy meter

Cause

The EBO trace log shows a lot of BACnet related error messages, such as:

 

nsp.pin.BACnet.VariableProperty Subscription to ~/BACnet Interface/IP Network/PM 5340/Application/THD Current - Ph G attempted COV, but will POLL due to BACnet error: 0x00030013 (resources,no_space_to_add_list_element)

 

This error indicates that a Change of Value (COV) subscription is being attempted but has failed. This is due to a resource issue with the device, i.e., error class 0x0003 from error code 0x00030013. The error is no space to write property (0013 part) which suggests the subscription limit of the device has been reached. Refer to the Decoding BACnet Errors Knowledge Base article for further information on decoding the error code.

 

Reviewing the PM5300 series user manual reveals that the device only supports 20 COV subscriptions.

PM5000COVLimit.png

 

 

Resolution

  1. Remove BACnet objects that are not required in EBO, it is unlikely that fewer than 20 values will be practical.
  2. Disable COV for the device in EBO. This can be done via the service_blacklist as noted in the BACnet RULES implementation to disable features such as readPropertyMultiple, COVs etc How to disabl... The following is an example service_blacklist for the PM3450
    <blacklist>
       <rule>
         <vendor>10</vendor>
         <model>PM5340</model>
         <no-cov/>
         <no-rpm/>
       </rule>
    </blacklist>
  3. Polling can put an unintended load on the polling device and the polled device. The polling intervals should be adjusted using the settings on the BACnet Interface. This is available from BACnet Interface -> Properties -> Advanced and scroll all the way to the bottom as shown below for an ES. If looking at the option for an Automation Server it will also have additional options for the RS485 communication ports. Minimum polling intervals in the range of 5,000 to 10,000ms are a good starting point.PollIntervals.png

 

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • CraigEllis23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of