Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PCT 1.x Connection Issue Error: "Get System State Command: 'Could not connect' "

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PCT 1.x Connection Issue Error: "Get System State Command: 'Could not connect' "
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Taylor_Leach
    Taylor_Leach
  • CraigEl
    CraigEl
  • StephenYang
    StephenYang
  • Jonathan
    Jonathan
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
12408 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PCT 1.x Connection Issue Error: "Get System State Command: 'Could not connect' "

Product_Support
‎2018-09-10 07:17 AM

Last Updated: CraigEl Champion ‎2024-01-16 05:33 PM

Issue

This condition will arise after successfully installing and running Project Configuration Tool for some time. PCT 1.x can no longer initialize the virtual host adapter as a result of the adapter being deleted or removed.

The errors may be a result of but not limited to:

  1. Introducing a new VPN software package to your PC/Laptop.
  2. Manually removing or modifying the Virtual Box Host Only - Network Adapter.
  3. Malware or Antivirus platforms that have removed or disabled the adapter.

Example:

PCT Version - 1.1.2.57 Local mode was set up on a physical laptop and used to offline engineer a project. The job was completed and PCT was not used again for roughly a month.

A new project was sold and required PCT for offline engineering. The laptop was booted up and PCT failed to open. The user was presented with the following errors:

  • "Get System State Command: 'Could not connect' "
  • "Get predefined properties command: 'Could not connect' "
  • "GetDashboardErrors Command: 'Could not connect' "
  • "Get System Memory info Command: 'Could not connect' "

Product Line

EcoStruxure Building Operation

Environment

  • Windows Client versions (64 Bit Only)
  • Windows Server versions (64 Bit Only)
  • PCT SERVER versions (64 Bit OS Only)
  • Project Configuration Tool 1.x

Cause

PCT 1.x can no longer initialize the virtual host adapter as a result of the Vbox adapter being deleted or removed.

Resolution

Reinstall PCT 1.x on top of your current installation. Your projects will not be modified in the process.

  1. Locate the installer.
  2. Run the installer, it will ask you to remove the previous version. Press ok.
  3. Progress will show as uninstalling.
  4. PCT will prompt for installation. Click Next.
  5. Select default installation paths. Click Next.
  6. Select desired PCT mode. Click next.
  7. Ready to Install selected mode. Click Next.
  8. PCT software installed. Click Finish.
  9. Now PCT will set up the Virtual Host Adapter. Press Ok.
  10. Status bar.
  11. Compted setup dialog. Click Ok.
  12. Run PCT. If successful you will see the template sets getting installed via the top right of the window.
  13. Open a project and test an AS/AS-P.

If the above steps do not work, here are a few more to try:

 

  • Restart the machine after the PCT software finishes re-installing
  • Right-click and select “Run as Administrator”
  • Uninstall PCT software and Oracle VirtualBox and re-install once more

 

If PCT 1.x still will not work, please open a support case with your local Product Support Group.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 19840
  • project configuration tool
  • StephenYang24
  • TaylorLeach19
  • vbox
Was this article helpful? Yes No
65% helpful (9/14)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore