Object type mismatch error when reloading inputs or output to a b3 Controller
  • Object type mismatch error when reloading inputs or output to a b3 Controller
  • RobertAndriolo
    RobertAndriolo
  • JohnBoehmer
    JohnBoehmer
‎2018-09-11 08:13 AM
During reloading of controller when physical points are reloaded a Object Type Mismatch error occurs.
  • b3
  • Reload
Controller database issue.
In this case the problem was resolved by...
  • Deleting the bacnet instance of the controller.
  • Deleting the Infinity instance of the controller in offline mode.
  • Relearning the controller.
  • Rebuilding the controller configuration manually.
  • Finding the bacnet device and sending to database.
  • 17985