New Alarm Enrollments don't work, existing enrollment work fine.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • New Alarm Enrollments don't work, existing enrollment work fine.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • BillNeville
    BillNeville
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1639 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

New Alarm Enrollments don't work, existing enrollment work fine.

Picard Product_Support
‎2018-09-10 11:34 PM

Issue

Created new Alarm Enrollment, attach to point and put point in alarm but no alarm is received and the points alarm value does not show the point is going in alarm.

No problem when using an existing Alarm Enrollment created in the past when the total number of Alarm Enrollment objects was much less.

Environment

  • CyberStation
  • CX9900
  • CX9640
  • CX9702
  • CX9680
  • ACX5720
  • ACX5740

Cause

Controller's handle id limit on Alarm Enrollment objects has been exceeded.

Resolution

Click here to download this article as a PDF: Continuum Alarm Enrollment Handle ID Limits

Continuum Alarm Enrollment Handle Ids Limit.

(Note the information presented here applies only to non BACnet alarms)

In Continuum there is a limit on the number of Alarm Enrollment objects that can be sent to the controller, the limit is 4000.

Unlike the BACnet alarms, the Continuum alarm enrollments are meant to be re-usable, the system was designed for the Alarm Enrollment to be reused hence the limit, when the system is used as designed is very unlikely if not impossible to exceed the 4000 Alarm Enrollment objects limit.

There have been cases where this limit has been exceeded due to site requirements that do not conform to the Continuum design, further more as of version 1.94 Continuum does not provided any feedback when the limit is exceeded, the alarm simply won’t work since the controller does not accept the alarm enrollment objects sent by the CyberStation.

Guidelines to avoid exceeding the alarm enrollment handle id limit.

  1. Re-use, re-use, re-use. The Continuum system was designed for the Alarm Enrollments to be reused.
  2. If for some reason the number of alarm enrollment object is approaching the limit, do not delete Alarm Enrollment objects, if you have an alarm enrollment that is no longer needed rename it and re-purpose it instead of deleting it and creating a new one, the reason for this is that the handle ids once assigned are never re-assigned, so if you delete an alarm enrollment its handle id is lost forever.

How to clean up if the limit is ever exceeded.

If there are any Alarm Enrollment objects with handle ids out of range in the database they should be deleted to avoid confusion but before they are deleted all links to the enrollments have to be identified and the links removed.

  1. To find any links to alarm enrollment objects with id out of range run the following query against the ContinuumDB
      Select * from EventEnroll where AlarmRefLo > 562041735
    If you get any results look at the uiName column, the uiName will consist of the point’s number and the AlarmEnrollment’s name separated by a period.
    Example: Num1.TempTooHigh
    Now From the Continuum explorer, find the point named ‘Num1’ that has a link to ‘TempTooHigh’ and remove the link.
  2. After all the links have been removed run the following query to find all the Alarm Enrollment objects with handle ids out of range.
      Select * from AlarmEnroll where ObjectIdLo > 562041735
    Note the name in the uiName column, from the Continuum explorer delete the AlarmEnrollment objects.
Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 12571
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore