NetController 2 IO Modules not powering up when using third party power supply
  • NetController 2 IO Modules not powering up when using third party power supply
  • Alan_Wood
    Alan_Wood
  • Dave_Shore
    Dave_Shore
‎2018-09-06 12:22 PM
Last Updated: Administrator CraigEl Administrator ‎2025-08-29 03:43 AM
NetController 2 IO Modules do not power up when using a third-party power supply.
Andover Continuum
  • NetController 2, NC2, NCII
  • IO Modules
When a third-party power supply (AC or DC) is used with the NC2, the IO modules do not receive power through the NC2 connector.
To ensure proper operation:
  • Use the Continuum Power Supply if you want the IO modules to be powered via the NC2 connector.
  • If using a third-party power supply, the IO modules must be powered separately.
Additional Notes
  • This behavior is documented in the official NC2 documentation.
  • Always refer to the product manual for detailed wiring and power requirements.