Multiple RTU Xdrivers on a single Netcontroller / BCX1/ ACX57xx / Netcontroller 2
  • Multiple RTU Xdrivers on a single Netcontroller / BCX1/ ACX57xx / Netcontroller 2
  • ScottLeedberg
    ScottLeedberg
  • Alan_Wood
    Alan_Wood
  • CraigEl
    CraigEl
‎2018-09-10 04:59 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:30 PM
Both comm ports can be enabled for RTU, but is this a recommended configuration?
Andover Continuum
  • Continuum
  • 9900
  • 9940
  • 9680
  • 9640
  • 5740
  • 5720
  • Xdriver
2 port can be enabled for RTU Xdriver on a netcontroller, but is this a recommended configuration or will this be too much of a strain on the Controller?
According to the Xdriver developers, it is NOT advisable to use 2 Modbus RTU Xdrivers on the same Controller
The Modbus RTU Xdriver is the only 'poll on demand' type xdriver and this dual configuration has the potential of holding the CPU for longer and could cause the polling to become irregular.
It is recommended to add an additional Controller to handle the additional devices and points required.
Also see
  • BCX Controller can use Comm 1, Comm2, or both ports for Modbus RTU X-Driver
  • Can two comm ports be enabled when using the RTU Xdriver?
Tags (2)
  • 6632
  • tcpip