Issue
Both comm ports can be enabled for RTU, but is this a recommended configuration?
Product Line
Andover Continuum
Environment
- Continuum
- 9900
- 9940
- 9680
- 9640
- 5740
- 5720
- Xdriver
Cause
2 port can be enabled for RTU Xdriver on a netcontroller, but is this a recommended configuration or will this be too much of a strain on the Controller?
Resolution
According to the Xdriver developers, it is NOT advisable to use 2 Modbus RTU Xdrivers on the same Controller
The Modbus RTU Xdriver is the only 'poll on demand' type xdriver and this dual configuration has the potential of holding the CPU for longer and could cause the polling to become irregular.
It is recommended to add an additional Controller to handle the additional devices and points required.