Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Multiple Automation Servers on the same backplane

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Multiple Automation Servers on the same backplane
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3227 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Multiple Automation Servers on the same backplane

Picard Product_Support
‎2018-09-10 11:27 PM

Last Updated: Picard RobertAndriolo Picard ‎2025-08-27 04:58 PM

Issue

Is it possible for multiple Automation Servers to be placed on the same backplane and use one power supply?

Some known issues in this unsupported configuration:

  • Automation Server only partially discovers the IO Modules
  • Function Block Programs (FBP) remain in an unloaded state (see FBP Unloaded)
  • EBO 2022 (v4.0) and higher, Alarm: IO Driver unexpectedly timed out
    AlarmView.png

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation Automation Server (EBO 2022 and above)
  • EcoStruxure Building Operation Power Supply (PS-24V)
  • EcoStruxure Building Central IO Modules

Cause

The terminal bases provide a path for communication between all connected units on the same backplane; as such, the connection of two or more Automation Servers will cause communication issues between all connected units on that same backplane.

See the following article on how to check the CIO node the Automation Server is using: How to identify Automation Server(AS) ID node count  

Resolution

From EBO 2022 (v4.0.1) due to changes in the Central I/O (CIO), checks are now made in the Automation Server to verify that the server is physically in SLOT 2; if this is not the case, then all Tasks are disabled and will not run. 

 

You cannot connect more than one Automation Server to the backplane. Only one Automation Server is allowed per power supply, the architecture is always "PS-AS-....." and after that I/O modules with additional PS units as needed, but only one Automation Server can exist on the same backplane.

 

Note that an alarm will also generate if you attempt the following configuration (also not supported) 

  • PS-AS-PS-AS 

Alarms will only clear after a restart (warm) of the server 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 12328
  • CraigEllis23
  • RobertAndriolo22
  • RobertAndriolo23
  • RobertAndriolo25
Was this article helpful? Yes No
100% helpful (6/6)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore