Modem to communicate with a GCM-86xxx controller when using XPSI 4.1
  • Modem to communicate with a GCM-86xxx controller when using XPSI 4.1
‎2018-09-10 05:13 AM
Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM
Can the XPSI 4.1 software communicate to a GCM via a modem connection?
TAC IA Series
  • XPSI/PSI 4.1
  • GCM-86xxx
  • GCM-84xxx
When capturing trend log data over an unapproved modem, the program lost sync with the incoming data after receiving about 10 lines of log data.
The only modem currently approved for communications with GCMs is the USRobotics 56k (USR5686E).
The configuration information for this modem was published in Technical Bulletin 00-47 with model update information published in Technical Bulletin TB03-04.
NOTE: If using the USR5686E with older modems, the V.92 communications protocol must be disabled -- see Modems fail to connect with the USRobotics 5686 series V.92 modems for details.