Modbus device is offline in Vista
  • Modbus device is offline in Vista
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • HenrikTarpgaard
    HenrikTarpgaard
‎2020-11-16 03:16 PM
on ‎2020-11-16 03:16 PM
Modbus device is offline in Vista.
TAC Vista
  • Xenta 511
  • Xenta 913
  • Xenta 700
The Modbus device online check has to read at least one variable for the device to come online in Vista. If you only write values to the Modbus device, it will appear offline.
As a workaround, you may create a dummy variable that you read from in Xbuilder
Tags (2)
  • 15633
  • PeterLarsen20