Maximum Distance for Installing xP Expansion Modules
  • Maximum Distance for Installing xP Expansion Modules
  • Alan_Wood
    Alan_Wood
  • Carl_Slack
    Carl_Slack
‎2018-09-06 01:20 PM
Last Updated: Administrator CraigEl Administrator ‎2025-08-29 04:31 AM
What is the maximum allowable distance for installing an xP expansion module?
Andover Continuum
xP Expansion Module
Clarification needed on the cable length limitations when connecting xP expansion modules to controllers.
xP expansion modules can be connected in two ways:
  1. Direct Connection:
    • Modules may be attached directly to the bottom of the controller using the built-in expansion port connector.
  2. Remote Connection via Ribbon Cable:
    • Modules may also be connected remotely using either:
      • A 3-foot (~1 meter) ribbon cable
      • A 10-foot (~3 meter) ribbon cable
    • Important: The total cable length used across all expansion modules must not exceed 10 feet (~3 meters).
Mounting Guidance:
  • Each xP module includes four mounting holes in the base plate for secure installation.
Additional Notes
  • Ensure proper cable management to avoid signal degradation.
  • Avoid exceeding the total cable length to maintain system reliability.