Mass firmware upgrade on multiple MPMs (bulk upgrade)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Mass firmware upgrade on multiple MPMs (bulk upgrade)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • SaidSawan
    SaidSawan
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1828 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Mass firmware upgrade on multiple MPMs (bulk upgrade)

Picard Product_Support
‎2018-09-10 06:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:50 PM

Issue

How to upgrade remote MPMs with a Canbus, Zigbee network.

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager MPM

Cause

Cannot connect to an MPM directly to perform a firmware upgrade

Resolution

This procedure explains how to perform a firmware upgrade on multiple remote devices at once, in order to save time and standardize the firmware versions across your deployment. This process will induce traffic on the network, therefore it is recommended that this procedure be performed after-hours or when it is less likely to disrupt normal operations.

Step 1: Verify your monitor Manager's firmware version

Ensure monitor MPM has the same or higher firmware version than the the version intended to be installed on the remote MPMs. Highlight the MPM in the Network Panel on the left side of your screen and either click on the "About" button or navigate to CFG1 object to verify firmware version.

1.jpg2.jpg3.jpg

Step 2: Download and rename the firmware file

The firmware can be downloaded from the Exchange then firmware file must be renamed "upgrade.bp"

Step 3: Upload the firmware file to your Manager

Choose the File Manager tab and click on the “Upload File” icon. A dialog box will open to select the firmware file on your local PC.

4.jpg

Browse to the correct file and select it. Click the “Upload” button to send the file from your computer to the controller.
When the file upload is completed, the file will be shown in the Upload Manager list.
 5.jpg


Step 4: Initiating the remote upgrade


Inside the File Manager panel, either right-click on the firmware file that was just uploaded and select “Add to all” to copy the same file to all the remote nodes, or drag and drop the file from the left panel onto the desired Manager on the right panel. The file will be displayed under each of the remote nodes (or a single node if the file was copied using drag and drop) under the Network panel, on the right side of the window.

 

6.jpg


In order to initiate the file transfer to the remote nodes, click the Start button. The status will change to “In Progress” and you will be able to follow the progress of each node in the Network panel. Once the file transfer is complete, the remote nodes will reset and perform the firmware upgrade.

Step 5: Verify the firmware version of the remote nodes


You can verify that the upgrade process completed successfully by highlighting the remote node in the left panel and then select the “Controller Configuration” (CFG1) object. The version # will be displayed in the bottom section.

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (1)
  • Find more articles tagged with:
  • 18327
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of