Manually Adding Xenta device with Group bindings in Lonmaker

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Manually Adding Xenta device with Group bindings in Lonmaker
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1211 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Manually Adding Xenta device with Group bindings in Lonmaker

Picard Product_Support
‎2018-09-06 03:50 PM

Issue

Can I add the group bindings manually as the option to create group binding in the System Plug-in takes time and controllers are taken offline for the period of the process

Environment

  • Lonmaker
  • Vista

Cause

This is  possible to do and works very well and effectively if you understand the process 

Resolution

Follow these steps to add TAG 0 system bindings and TAG 1 Xenta bindings to your new Xenta controller.

  1. In Lonmaker find the source of the TAG 0 binding buy finding any TAG 0 existing binding.
  2. Then right mouse click on the tag number and select Go to reference.
  3. This will take you to the source of the TAG 0 bindings. If a list of controllers appear then you are already at the source controller.
  4. Then Carry out a connection as normal in Lonmaker on that function block.
  5. Right click on the Virtual function block with the TAG 0 source and select the connect option.
  6. Select the TAG 0 option under the Hub tab then select the target tab and add the new Xenta controller to the system with the Add FB/SNs button.
  7. Then select the TAG 0 in the virtual function block of the new Xenta and click on the Add button. The select the OK button.
  8. This will add the TAG0 binding to the new Xenta device with the correct binding type.
  9. The next step is similar to the TAG 0 but for the TAG 1. You need to locate the TAG 1 Xenta group that you are adding the new Xenta controller into.
  10. Once you have located the TAG1 source use the same connection method as TAG0 but use the TAG1 in the virtual blocks.
  11. The final step is to download the added controller and the group master.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7902
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore