Managing communication between I/NET and StruxureWare

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Managing communication between I/NET and StruxureWare
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3948 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Managing communication between I/NET and StruxureWare

Picard Product_Support
‎2018-09-10 07:12 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:07 PM

Issue

Managing communication between I/NET and StruxureWare

Product Line

EcoStruxure Building Operation, TAC INET

Environment

  • I/NET Enterprise server level integration
  • I/NET Automation server level integration
  • StruxureWare Building Operation 1.6.1.5000 and above.

Cause

Users should manage data flow on the controller LAN in order to maintain efficient communication.

Any binds to objects under the I/NET interface follow the settings for the INET Global device scan rate (min) and the INET Global point scan rate (s). By default, this is set to 60 minutes for device status and 5 seconds for point bindings.

The INET Global device scan rate (min)  is used to monitor online devices. A device will show offline sooner than the configured setting as all points would show offline. 

The  INET Global point scan rate (s) is applied to all binds between StruxureWare and I/NET.  Opening a graphic or watch window will ignore this rule and immediately request values. After that, the scan will update according to the configured setting.

A controller can either follow the Global scan rates as by default or use its own setting.  When a controller has the property DCU scan rate or point scan rate set to 0, it will follow the scan rate configured for the I/NET interface.

An I/NET 19200 speed Controller LAN will handle a maximum of 10 token cycles per second. Each cycle allows a single packet of information to be passed from a single controller to the server. 1 Packet can contain all data for up to 18 points on a single controller. This means binding to manual, value, and PvControl for 18 points on a single 7718 will take one packet. Binding only the value of 5 points on 5 different controllers will take 5 packets. Adding devices to the controller LAN and adding additional polling will slow down the number of cycles per second on the controller LAN.

Resolution

All active binds will poll every scan interval. Graphic binds are only active when the graphic is open. Trend Logs will poll every scan interval regardless of the log configuration options. 

Whenever possible, use the I/Net Alarm and Trend objects rather than creating separate StruxureWare alarm and trend objects.

Trend Log Best Practices:

  • Use the I/NET Trend Extension as outlined in Using I/NET trends in StruxureWare Building Operation please refer to the online help guide for complete information.
  • Create Extended Trend Logs of this information for long term storage.

I/Net Alarm Best Practices:

  • Use the I/NET point extension to configure the alarm to be triggered by logic within the I/NET controller.
  • I/NET Alarms have 3 priority options which are Routine, Priority, and Critical. This can be globally assigned to any priority using the I/NET interface messages tab.
  • Other StruxureWare Alarm enhancements are available to I/NET objects as well.

Scheduling and programming I/NET from StruxureWare

  • Whenever possible, bind values to a single I/NET controller per controller LAN and then create I/NET Global/Indirect point relationships to distribute this value to other devices on the controller LAN. Using a single controller allows more information to be sent per packet. I/NET Global points will only broadcast on change. In this scenario, the server is polling a single controller ever scan interval and then on change all other controllers are updated.

Increase the Point scan rate

  • Using the information above you should be able to calculate how many packets are required for your system for each token pass. If this number increases to the point that more packets are required than are possible in the default 5 seconds, increase the scan rate. You can increase it on specific over loaded controllers or on all controllers together.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
Tags (9)
  • Find more articles tagged with:
  • 18215
  • adapter
  • asp
  • having
  • seeing
  • trouble
  • usb
  • while
  • writing
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore