Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Managing Concurrent User Limits in Vista Webstation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Managing Concurrent User Limits in Vista Webstation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen
  • DavidFisher
    DavidFisher
  • sesa150561
    sesa150561
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3661 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Managing Concurrent User Limits in Vista Webstation

Picard Product_Support
‎2018-09-06 10:58 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-21 06:53 PM

Issue

Users are unable to access Webstation due to the system reaching its maximum number of concurrent user sessions.

Product Line

TAC Vista

Environment

TAC Vista Webstation

Cause

Webstation enforces a limit on the number of simultaneous user sessions based on the license configuration. When this threshold is reached, additional login attempts are blocked.

License Types and Limits

License Type Description
0-008-8270-1 Vista 5.1 Webstation 1 CAL – One concurrent user
0-008-8271-1 Vista 5.1 Webstation 3 CAL – Three concurrent users
0-008-8272-1 Vista 5.1 Webstation 6 CAL – Six concurrent users
0-008-8273-1 Vista 5.1 Webstation 12 CAL – Twelve concurrent users
0-008-8274-1 Vista 5.1 Webstation Unlimited – Unlimited users

Additional Considerations

  • Operating System & IIS Limits: These may impose additional restrictions not directly related to Webstation licensing.
  • Windows XP: Limited to 10 connections due to TCPIP.SYS, resulting in error 403.9 – Access Forbidden: Too many users.
  • Windows 7 (SP2): Connections beyond the limit are queued, causing delays but no error messages.
  • Windows Server Editions: No connection limits – recommended for hosting Webstation.

Note: Each Webstation session uses 1 connection. Each open TGML page also uses 1 connection. For example, 1 Webstation + 5 TGML pages = 6 connections.

Resolution

Recommended OS Configurations

OS Version IIS Version Connection Limit Notes
Windows Server 2008 R2 IIS 7.5 No Limits Recommended
Windows 7 (Ultimate/Enterprise/Business) IIS 7.5 10 Allows multiple sites
Windows Vista (Ultimate/Enterprise/Business) IIS 7.0 10 Allows multiple sites
Windows XP Professional IIS 5.1 10 Only one site
Windows 2000 Professional IIS 5.0 10 Only one site
Windows NT 4 Workstation IIS 4.0 No IIS PWS installs via NT Option Pack

Best Practices

  • Use Windows Server OS for production environments to avoid connection limits.
  • Monitor TGML usage to optimize connection consumption.
  • Consider upgrading license if user demand exceeds current CAL limits.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 11512
  • PeterLarsen25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore