Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Maintaining data when replacing a legacy device with a new generation device

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Maintaining data when replacing a legacy device with a new generation device
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1364 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Maintaining data when replacing a legacy device with a new generation device

Picard Product_Support
‎2018-09-11 12:56 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:46 PM

Issue

A site has to replace a legacy device with newer hardware and wants a continuity of values being read into trend logs.

Product Line

EcoStruxure Building Operation

Environment

This has been tested for I/NET hardware replacement, but the process will work for any device which has values stored in the Extended Trend Log

Cause

The Extended Trend Log allows users to change the Monitored trend log attribute as needed for continuity of data. This process can be used to ensure that regulations are met regarding requirements for trend data.

It is important to ensure that the new trend log is created in such a way that no significant time is lost between samples on the old log and samples on the new log. The Extended trend log will be the warehouse for the long term data of the two source logs to be stored. 

Resolution

  1. In this example we are looking at an Extended Trend Log which has been collecting values for some time.
  2. To Ensure all values are transferred from the Old Log to the Extended Trend Log, Right-Click on the Extended Trend Log and select Activation>Force Transfer
  3. Edit the Properties of the Extended Trend Log and delete the Monitored Trend Log which was monitoring the old input value.
  4. Save the change to the Extended Trend Log. At this point the log will no longer collect data from it's original input source
  5. Locate the new location of the value being monitored. This could be the input an Automation Server, Field device or a logical output of a program.

    NOTE: Steps 6-9 show the basic process for creating an Interval Trend Log. This may change depending on the new device type or location. For creating I/NET trends, please see Using I/NET trends in StruxureWare Building Operation
     
  6. Right Click on this new object and select New>Trend
  7. Select the identical type and use the identical (or similar) configuration settings.
  8. Click OK
  9. View a Trend Log list of the new Trend log to verify that it is functional.
  10. Edit the Properties for the Original Extended Trend Log
  11. Click on the ellipsis to change Monitored Trend Log setting so that the Extended Trend Log now references the newly created trend log.
  12. Save the Changes
  13. Right click on the Extended Trend Log object and select Activation>Force transfer.
  14. View the Extended Trend Log list. You should see the new values after the record of the property changes.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 18383
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore