Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

MS/TP and Modbus RS485 Communications on StruxureWare Automation Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MS/TP and Modbus RS485 Communications on StruxureWare Automation Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa177673
    sesa177673
  • sesa125819
    sesa125819
  • RandyGo1
    RandyGo1

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
10887 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MS/TP and Modbus RS485 Communications on StruxureWare Automation Server

Product_Support
‎2018-09-11 06:44 PM

Last Updated: CraigEl Champion ‎2022-08-07 11:02 PM

Issue

Both BACnet MS/TP and Modbus typically provide a robust and reliable communications channel allowing the Automation Server to effectively manage a large collection of equipment over extended distances. When the system does not come up operating as expected due to the communications integrity, considerable effort can be consumed troubleshooting or working-around the fault observations.

Product Line

Andover Continuum, EcoStruxure Building Operation, Field Devices, Other, TAC IA Series

Environment

Automation Server with BACnet MS/TP or Modbus RS485 networks connected to Port A or Port B.

Cause

The configuration of the RS485 network can create conditions that reduce the tolerance for EMI noise on the bus, electrical ground differences, transmission signal loss through the cable and/or component performance.

Resolution

A collection of application notes and Quick Start Best Practices Guides are available on the subject of BACnet MS/TP and Modbus RS485 network connections to the StruxureWare Automation Server.  These application notes and quick start guides provide recommendations in the areas of –

  • BACnet MS/TP & Modbus RS485 Network Termination
  • Network Biasing Options and Techniques
  • Unit Load and associated Maximum Node Count Recommendations
  • Isolated RS485 Interfaces and related Expanded Unit Load
  • Cable Specifications and Suggested Cable Selections
  • Cable Routing and Recommended Lengths

The documents describe configurations of cable, network length, node counts and bias arrangements providing compliance with the EIA/TIA-485 Standard and TSB-89-A Guidelines with the objective of optimizing system tolerance for noise, grounding and transceiver component variations.  Most of the application notes and quick start guides target specific product families which include the Andover Continuum b3 Family, TAC I/A Series MNB Family, Legrand Power Meters and the Viconics VT7000 series sensors. There is also an application note and quick guide directed toward other “Generic” RS485 MS/TP and Modbus devices where the user is guided through a sequence of information collection steps to determine the appropriate recommendations. 

The collection of application notes and guides are available on the Schneider Electric download center. The list of links below will take you to the applicable download page.

  • AN01-RS485-Generic Application Note – General MS/TP & Modbus I/F to Automation Server
  • Quick Guide-RS485-Generic Best Practices Guide - General MS/TP & Modbus
  • AN02-RS485-B3 Application Note – Continuum B3 I/F to Automation Server
  • Quick Guide-RS485-B3 Best Practices Guide - Continuum B3 I/F
  • AN03-RS485-MNB Application Note – I/A Series MNB I/F to Automation Server
  • Quick Guide-RS485-MNB Best Practices Guide – I/A Series MNB I/F
  • AN04-RS485-Legrand Application Note – Legrand Meter I/F to Automation Server
  • Quick Guide-RS485-Legrand Best Practices Guide – Legrand Meter I/F
  • AN05-RS485-VT7000 Application Note – VT7000 Series I/F to Automation Server
  • Quick Guide-RS485-VT7000 Best Practices Guide – VT7000 Series I/F

Note:    If using the download center for the first time, you will need to register. See Register for The Exchange Download Center for more information. The Download Center requires the use of Internet Explorer (version 8 or higher), Google Chrome or Firefox browsers.

Additional information is available in the Hardware Reference Guide

Access the StruxureWare Building Operation Web Help.

Also check out the SmartStruxure-RS485-Controller Unit Load Quick-Help video on the Exchange.

Labels (4)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • TAC IA Series
Tags (5)
  • Find more articles tagged with:
  • 120ohm
  • 15478
  • 180ohm
  • backbone
  • belden
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore