MN-LCD Uploading – Best Practices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MN-LCD Uploading – Best Practices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1998 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MN-LCD Uploading – Best Practices

Picard Product_Support
‎2018-09-06 01:23 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-23 06:29 PM

Issue

Micronet LCDs may fail to upload configurations from MicroNet controllers correctly, leading to incomplete or missing display data.

Product Line

Satchwell MicroNet

Environment

  • MicroNet LCD Displays
  • MicroNet Controllers
  • VisiSat Configuration Tool

Cause

The upload failure typically occurs when the LCD configuration is not properly transferred from the controller’s RAM to the LCD’s EEPROM. This can happen due to:

  • Power cycling or resetting the controller before LCD connection
  • Incorrect connection sequence
  • Locked configuration settings in VisiSat

Resolution

Follow these steps to ensure successful upload and avoid data loss:

How the Upload Process Works

  1. Download to Controller: LCD configuration is first downloaded to the controller’s RAM.
  2. Transfer to LCD: When the LCD is connected, it detects the configuration file and transfers it to its EEPROM.
  3. RAM Clearance: After transfer, the controller’s RAM copy is deleted.
  4. Important: If the controller is powered off or reset before the LCD is connected, the configuration will be lost.

LCD Download Procedure

  1. Power On Controller: Ensure the controller is powered before starting.
  2. Download Configuration via VisiSat.
  3. For Standalone NCP Controllers:
    • Disconnect communications before connecting the LCD.
    • Ensure LCD comms links are properly fitted.
  4. For Networked NCP Controllers:
    • Install an MNN-COM card.
    • LCD must be remotely mounted.
  5. Connect LCD:
    • Keep controller power ON.
    • Apply power to the LCD.
    • Note: Do not press any keys during connection unless using firmware revision J or earlier.
  6. Wait for Configuration Load.
  7. Troubleshooting:
    • If upload fails, check that the controller’s “Configuration Locked” property is set to No in VisiSat.
  8. Final Step: Remove the protective strip from the LCD battery.
Labels (1)
Labels:
  • Satchwell MicroNet
Tags (2)
  • Find more articles tagged with:
  • 6003
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore