Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Lon comms card will not work on HP 6560D Probook Laptop running on Windows XP

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Lon comms card will not work on HP 6560D Probook Laptop running on Windows XP
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1290 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Lon comms card will not work on HP 6560D Probook Laptop running on Windows XP

Picard Product_Support
‎2018-09-11 01:01 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:10 PM

Issue

The Lon comms card that can be installed in the pciExpress slot on HP Laptops can sometimes generate a "Buffers Full" error. The identical fault details can be found in another Knowledge Base article relating to Dell E6400 laptops.

Product Line

Satchwell MicroNet, Satchwell Sigma, TAC Vista

Environment

  • Sigma using IC-3 Lon with Lonmaker for Windows
  • Vista
  • Micronet when using Lon interface
  • Using the Lon PCC-10 Card in a laptop that has an express card slot and not a PCMCIA card slot.

Cause

There is an issue with some HP 6560D Probook laptop that is provided by the UK IS department to commissioning and service engineers. If they need to use the Echelon Lontalk PCC-10 PCMCIA card then when trying to configure it via the Control Panel applet it will fail giving an error message "Driver Buffers Full" or it will simply fail when running diagnostic tests.

Resolution

See Can a LON PCC-10 PCMCIA card work in a laptop with an express card slot? for details of the Express card configuration for laptops.

Labels (3)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 12666
  • ftt-10
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of