Limits on the number of controllers in a Continuum System

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Limits on the number of controllers in a Continuum System
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2349 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Limits on the number of controllers in a Continuum System

Picard Product_Support
‎2018-09-11 12:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:11 PM

Issue

What is the limit of the number of Controllers that can be in a Continuum System?

Product Line

Andover Continuum

Environment

Continuum

Cause

Want to know the theoretical and practical limits to how many controllers can be on one system.

Resolution

There are certainly some logical limits to how your Netcontrollers are addressed and identified in the system but for all intents and purposes you are only restricted by the IP Address.

Netcontrollers

Logically, you can have Netcontrollers addressed from 1 - 190 - so the maximum you can have in a "logical" Network is 190 Netcontrollers. However, the number of Networks you can have in a Continuum Database is only restricted by the Database itself - effectively infinite. See the article below on logical Networks.

How many logical networks can be created on a Continuum system?

This restriction is only for Netcontrollers defined within the Infinity side of the Continuum Database and does not apply to third-party BACnet controllers.

Field Controllers (b3 / i2)

There is a definite limit to the number of subnet (Infinet or MSTP) controllers that can be strung off of a given bCX or Netcontroller. As a general rule, each comm port can support up to a maximum of 127 subnet devices. Of course this does depend on the device being used, the amount of nodes it is enabled for, and the physical installation. The number of nodes purchased does correspond to the total number of i2 or MSTP controllers that can be on that bus.

Example: If you have a bCX1 with 32 MSTP nodes this means that a total of 32 MSTP devices can be on this MSTP network and the following architecture is valid.

bCX1 with bLink;

  • (segment1) node1 to node16.
  • (segment2) node17 to node32.

If we look at a Netcontroller or Netcontroller II, these controllers have two RS-485 comm ports that can be used to support Infinet subnet controllers, up to 127 on each port and a maximum of 254 off the one controller. Now the controller would need to have both ports enabled for 127 nodes and considerations made for the amount of traffic this number of controllers would require.

Similarly, the bCX1 (BACnet) will support up to 127 nodes. One thing to note is that this also includes repeaters if they are used to extend your network or star the MSTP.

The general rule for the number of devices on an MSTP segment is a maximum of 32 nodes, this dependent on the network complying with MSTP installation guidelines for termination, distance, cable type, and that each node is a full load RS-485 transceiver.

In the case of our BACnet controllers, they use a 1/4 load transceiver so given perfect network conditions it is possible to have 127 b3 devices on the same MSTP network segment. Even though this is possible, it is always good practice to use a b-Link repeater and a max of 32 devices per network segment - this also helps to segregate the devices for troubleshooting as well.

Total Point Limits

Other than with a Cyberstation with an I/O limited Security Key, I'm not aware of any limits to the number of points that can be created in a Continuum Database; this would be limited to the size and resources of the Continuum SQL Database.

Consult the following article that has a spreadsheet to help estimate the size of your Continuum Database. It could also help to estimate your SQL requirements: Continuum Database Sizing and SQL Server selection

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 12227
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of