Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Limit of how many devices a BACnet controller can know about (Known devices)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Limit of how many devices a BACnet controller can know about (Known devices)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • Cody_Failinger
    Cody_Failinger
  • DavidChild
    DavidChild
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • sesa101527
    sesa101527

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5591 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Limit of how many devices a BACnet controller can know about (Known devices)

Picard Product_Support
‎2020-09-07 07:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 10:52 PM

Issue

What is the limit of how many devices a BACnet controller can know about (Known devices) and what does that mean.

Product Line

Andover Continuum

Environment

  • BACnet bCX
  • bCX4040

Cause

More details required about Known devices

Resolution

The known device limit of a Continuum Ethernet level BACnet controller is 255 and for a B3 level MSTP controller it is 32.

This limit means is if a controller needs to either subscribe to a COV from another controller or deliver alarms (Event notifications) to a workstation, that each one of these target devices is a known device.

So, for example, if a b3 controller is subscribing to COV's from 30 other controllers and needs to deliver alarms to 3 WorkStations, it would require 33 known devices and the last request for a target device would fail. If a Controller is making 30 COV Subscriptions from one a single controller that would only count as 1 known device.
This limit does not apply to the number of other controllers which a COV exporter can deliver COV data to. For example, if a controller had a global point (OAT) that 50 other controllers needed to subscribe to, this is allowed because each COV subscription has within it the target controller's address information and does not use the known device limit. There are two cautions that must be considered.

  1. Refer to What are the differences between Standard Continuum Import/Export and Continuum BACnet COV?.
  2. Each COV subscription in an exporting controller takes away user memory. Each subscription uses approximately 56 Bytes of user memory. So the limit of how many other devices can subscribe COV's in an individual controller is limited by free memory in the exporting controller.

NOTE: To reset  the known devices following a change in the Controllers that will effect the number of known devices, the controller needs to be reloaded.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 2558
  • DavidShore20
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore