Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Large number of Log Data Transfer Missed events being logged

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Large number of Log Data Transfer Missed events being logged
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3880 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Large number of Log Data Transfer Missed events being logged

Picard Product_Support
‎2018-09-11 03:03 PM

Issue

A large number of "A Log Data Transfer Has been Missed" events are being reported by the AS.

All events are associated with b3 points that have intrinsic logging configured (where log configuration is part of the point properties configuration) and a StruxureWare Building Operation Extended Trend Log is attached to the point.

Product Line

EcoStruxure Building Operation

Environment

  • b3
  • Log Data Transfer
  • Extended Trend Logs

Cause

We have seen these events reported when the number of log records configured in the b3 point is not evenly divisible by the Maximum Log Transfer Interval in the Extended Trend Log object.

When the Extended Trend Log retrieves data from the objects intrinsic log in the b3 controller, it grabs this data in batches or portions.

The size of these portions is defined by the Maximum Transfer Interval in the Extended Trend Log configuration.

For example, where a b3's intrinsic log is set to 1 hour Log Interval and the Log Records is set to 72 (three days), if its associated Extended Trend Log has a Maximum Transfer Interval of 1 Day, the it will grab the first 24 records during the first pass, the next 24 records during the second pass and the remaining 24 records during the last pass.

If the number of Log Records defined in the point configured is 80 instead of 72, the same Extended Trend Log will grab the remaining data in a fourth pass.

However, if the amount of data remaining to be grabbed does not represent a span of time equal to the Maximum Transfer Interval, the Extended Trend Log will not grab a full period of data.

In some cases when this happens data from this fourth pass can be lost and this will be reported as an "A Log Data Transfer Has been Missed: event.

Example:

Using our example above, and an intrinsic log Record Count of 80, the Extended Trend Log will grab the first 24 records during the first pass, the next 24 records during the second pass, the next 24 records during the third pass. It will then grab the last eight log records in a fourth and last pass. It is during the transfer of this last smaller group of data where there may be a failure of the data transfer.

Resolution

The number of Log Records configured in the points intrinsic log times the Log Interval should equal a period of time that is evenly divisible by the Maximum Transfer Interval time period.

For example, if the Extended Trend Log is configured for a Maximum Transfer Interval of 24 hours, and the b3 point is configured for a 15 minute Log Interval, the Log Records can be set to either...

  • Log Records = 96 (4 samples per hour X 24 hours -- a full days worth of data)
  • Log Records = 192 (4 samples per hour X 48 hours -- two full days worth of data)
  • Log Records = 288 (4 samples per hour X 72 hours -- three full days worth of data) and so forth.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 16929
Was this article helpful? Yes No
50% helpful (2/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.