Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

LNS database in Vista by using L-IP and NIC852 Recommendations

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LNS database in Vista by using L-IP and NIC852 Recommendations
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • Anonymous user

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1150 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LNS database in Vista by using L-IP and NIC852 Recommendations

Picard Product_Support
‎2018-09-10 05:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:00 PM

Issue

  • How to estimate the amount of equipment needed for a LNS Vista system?
  • What are the recommendations and limitations for LNS Vista system?

Product Line

TAC Vista

Environment

  • LNS database
  • TAC Vista
  • Loytec L-IP
  • NIC852

Cause

It is very important to plan ahead when designing an LNS database in Vista in order to have a stable, robust system. Listed here are some recommendations for LNS database in TAC Vista.

Resolution

  • One LNS database can support up to 3000 devices. 
  • Each channel can have max. 100 devices (with repeater).
  • Use one L-IP per building or do not share devices among buildings under one L-IP. Otherwise, need to run the FT-10 wire between buildings.
  • If possible, create one LNS database per building. This is easier for trouble shooting and maintenance purposes. Then, use a NIC852 in order to manage multiple LNS database in one Vista Server. Follow the rules as below:
    • Without NIC852, one Vista server can only take up to 4 LNS databases. (With large LNS database, number will decrease.)
      NOTE: NIC852 is not required in this case, but recommended for large networks in order to achieve better performances
    • With one NIC852, Vista server can take up to 7 LNS database. (There are 8 ports on NIC852, but Vista server takes one.)
    • One Vista sever can take up to 4 NIC852. Therefore, one Vista sever can take up to 31 LNS databases. (Suggestion: do not extend 30 LNS databases, and better keep the number under 28.)
  • If additional Vista servers are required, a multi-server system can be used.  (It is recommended to not use more than 10 servers together for best performance.)

For Xenta Group and Xenta programmable controller specifications in a LNS database, please read Xenta Group and Xenta Programmable Device specifications for an LNS system.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5388
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of