Issue
Xenta Group and Xenta Programmable Device specifications for an LNS system
Network communication errors
Environment
- Vista
- NL220
- LonMaker
- Vista System Plug-in
Cause
Improper configuration of Xenta Programmable controllers will result in poor network performance
Resolution
Design Each LNS database within the following limits
- A maximum of 400 Xenta Programmable devices
- A maximum of 30 Xenta Groups
- A maximum of 30 devices with-in each Xenta Group
- Xenta groups should not have members separated by a router