LG BACnet Over IP Gateway
  • LG BACnet Over IP Gateway
  • CraigEl
    CraigEl
  • StephenYang
    StephenYang
‎2018-09-10 10:23 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-14 05:48 PM
Can't communicate with more than 1 device on LG Gateway at the same time.
Updated with solution on 12/15/2017
LG Gateway
Model:PQNFB17C1
Firmware version: 1.11.4
The gateway can only provide one source address when there are multiple device IDs. The wireshark capture confirmed that no unique source ID provided by the gateway with different device IDs.
Update the firmware version to 5.08.1h
Configure the "BACnet Type Setting" to "B Type".
  • 19514