Issue
Problem with redirecting a $EE_Mess alarm using "Configure alarms" in the Vista server. The alarm is not redirected to the new alarm object and therefore not changing the priority.
Product Line
TAC Vista
Environment
TAC Vista Server 5.1.6
Cause
$EE_Mess should be redirected to message object in Vista.
A change of state should be redirected to another change of state object in Vista
Resolution
Redirect the $EE_Mess to a message object in Vista and not to a change of state.
Refer to How to redirect a offline alarm to a certain alarm control object in Vista? for a guide on how to create a system alarm to handle offline alarms