Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Installing multiple Xenta Servers on a Lonworks network.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Installing multiple Xenta Servers on a Lonworks network.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1923 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Installing multiple Xenta Servers on a Lonworks network.

Picard Product_Support
‎2018-09-10 01:00 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:49 AM

Issue

Only one Xenta Server can be installed in Vista on a single Lonworks network.

Product Line

TAC Vista

Environment

  • TAC Vista
  • Lonworks
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913

Cause

When a Xenta 500/700/913 is installed in Vista as a Xenta Server, it is intended to act as the Lonworks network interface for Vista. By default, the Xenta 500/700 also handles the alarms generated in devices on the Lonworks network.  Only one Xenta Server can, therefore, exist on a single Lonworks network.  To enforce this, Vista does not allow you to add a Xenta Server to an existing Lonworks network.

Resolution

Install the first Xenta 500/700/913 device as a Xenta Server. Install any additional Xenta 500/700/913 as Lonworks Devices on the network.

As the Xenta Server handles the alarms generated in devices on the Lonworks network, the additional Xenta 500/700s must be prevented from handling alarms. This is done by changing the Alarm Server setting in XBuilder to 'Disabled'.

The XBuilder projects for the Xenta 500/700/913 configured as Lonworks Devices cannot be accessed from Vista.  In A LNS environment, SNVTS will be able to be seen through Vista workstation but no XBuilder parameters. These XBuilder projects must be treated as standalone and an XBuilder project backup is managed from outside the Vista database.

 

For details on configuring multiple Xenta 500/700/913s in Classic and LNS networks see these manuals:

TAC Vista - Classic Networks - Technical Manual

TAC Vista - LNS Networks - Technical Manual

TAC Xenta Server - TAC Networks - Technical Manual

TAC Xenta Server - Gateway - Technical Manual

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 7383
  • PeterLarsen20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore