Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Indirect Points going Old and causing system shutdown

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Indirect Points going Old and causing system shutdown
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1279 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Indirect Points going Old and causing system shutdown

Picard Product_Support
‎2018-09-06 01:45 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:17 PM

Issue

When points show Old Data some processes may cause equipment to shut down.

Product Line

TAC INET

Environment

I/NET

Cause

When a value is out of range in I/NET, any control referencing it will also be out of range.  For systems with communications issues this can be a problem for indirect points such as Outside Air Temp.

DDC modules contain a Failsafe Output Control Point which can also over come this obstacle.

Resolution

Refer to What does it mean when a point goes "OLD" in I/NET? with information on how to prevent points from going "Old".  If the point continues to go old you can use this process to account for the old point:

For this example assume that you are monitoring OAT with an indirect point

  1. Connect to the controller with the indirect point that is going old. (OAT)
  2. Create a duplicate of this point that is internal.  Call it "OAT_mirror" ensure that it has a relatively short scan interval
  3. Add a Calculation to OAT_mirror
  4. Use this expression: AV(P0,P1)  
  5. Set P0 as OAT
  6. Set P1 as OAT_mirror
  7. Click okay
  8. Change any control logic referencing OAT so that it references OAT_mirror

Results:

  • The AVG calc function will ignore any old value.  This means that while the OAT point is valid the OAT_mirror will quickly change to equal to it.
  • When the OAT point goes old the OAT_mirror point will retain it's current value until the OAT point is no longer old.

For information about triggering an alarm when a point goes old, view Triggering an alarm or message if a point goes old in I/NET

For further Indirect Point "Old Data" Filtering Techniques read I/NET Indirect Point "Old Data" Filtering Techniques

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5431
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore