What does it mean when a point goes "OLD" in I/NET?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What does it mean when a point goes "OLD" in I/NET?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Derrick_Ratliff
    Derrick_Ratliff

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1336 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What does it mean when a point goes "OLD" in I/NET?

Picard Product_Support
‎2018-09-07 03:48 AM

Issue

What does it mean when a point goes "OLD" in I/NET?

Product Line

TAC INET

Environment

I/NET

Cause

Points are labeled as old when the value is invalid or the point is no longer communicating. Here are possible reasons a point shows up as "OLD" or "old data"

  1. The SubLAN or UC device is offline or not communicating. In this case all points on the device will show as "old data"
  2. Indirect points are flagged as "Old" anytime an update request is initiated and no response is received from the global point for 2 scan intervals.
  3. If the sensor on an input produces a number either lower than the low sensor limit or higher than the high sensor limit the point will go old.
  4. DDC control logic outputs a value out of range of the point
  5. SubLan Communication error
  6. Improper global level on sending controller

Resolution

  1. The SubLAN or UC device is offline or not communicating. In this case all points on the device will show as "old data"
    Check to ensure the device is powered up and check physical communication. Ensure that the device is enabled in MCU Configuration and verify that the correct device type is specified.

  2. Indirect points are flagged as "Old" anytime an update request is initiated and no response is received from the global point for 2 scan intervals.
    Check the scan intervals of the indirect point and increase it to a larger setting. See TCON300 for details about how information requests are send between global and indirect points. A long scan interval will not translate to a delay in information being sent. Also check the communication path between the 2 points and ensure all equipment is working properly. For example if there is a known issue with an NPR that has global points underneath it, then all indirect points referencing those global points will frequently go old.

  3. If the sensor on an input produces a number either lower than the low sensor limit or higher than the high sensor limit the point will go old.
    Check the sensor and determine if it is faulty. If the value that is being sent is acceptable then increase and decrease the High and Low Sensor limits. This can also be caused by a sensor being disconnected.

  4. DDC control logic outputs a value out of range of the point
    Check all points that the DDC references and determine which is going old. Use Failsafe commands whenever available.

  5. SubLan Communication error
    Check the physical condition of the wiring on the SubLan. Determine if any SubLan device is faulty and interrupting communication.

  6. Improper global level on sending point
    Connect to the controller with the sending point and check it's global level. if the receiving point is on the same physical controller LAN wire you can set this to "LAN". If not, set it to "System"
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 4248
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of