Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

I/NET compatibility with EcoStruxure Building Operation 3.0.1 and higher

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET compatibility with EcoStruxure Building Operation 3.0.1 and higher
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • JonGreen
    JonGreen
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3068 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET compatibility with EcoStruxure Building Operation 3.0.1 and higher

JonGreen Mentor
‎2019-08-21 07:49 AM

Last Updated: RobertAndriolo Champion ‎2021-06-03 04:28 PM

Issue

  • Upgrading from EBO 2.0.x to 3.0.x causes I/NET to become incompatible.
  • After upgrading to 3.x the I/NET controllers do not come online.

Product Line

EcoStruxure Building Operation, TAC INET

Environment

  • EcoStruxure Building Operation (version 3.0.1 and later)
  • I/NET Seven Software (version 2.44 and above)

Cause

I/NET Seven Software is built using a 32-bit interface. Starting with EBO 3.0.1, EcoStruxure requires the use of a 64-bit interface.

Resolution

For INET seven to operate with EcoStruxure Building Operation 3.0.1 it is necessary to
obtain a 64-bit DLL from the Exchange and install it in the INET installation prior to the
upgrade.

  1. Search for INET IPortAPI64 - Software on Exchange. 
  2. Download the IPortAPI64_EBO.dll.
  3. Unzip the DLL and copy the DLL to the same folder as the 32bit INET install, by default this will be C:\Program Files (x86)\INET Seven folder.
    • Note: if INET was installed in a different folder this can be found by examining the
      Windows registry key ”INETSevenPath” at HKLM\SOFTWARE\WOW6432Node\CSI -
      Control Systems International\I/Net 2000/Configurations.
  4. Install EcoStruxure Building Operation 3.0.1
  5. When the ES restarts the InetPlugIn will connect to InetIoSrv via the 64-bit IPortAPI64_EBO.dll.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • JonathanGreen19
  • RobertAndriolo21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore