Issue
Some issues which this article covers are:
- What rules or recommendations should be used with Indirect and Global Points?
- Why might a global point not change?
- Attempting to alter a global AO/DO points' value/state, by "Point Control" without "Manual Mode" being used, and the change does not take place. (Referred to as Global Output Retentive Feedback.)
- What scan rates should be used for global / indirect points?
Product Line
TAC INET
Environment
I/NET Software
Cause
Often within a system, a point's status or value within one controller has to be shared or used in other controllers connected to the system. An example could be an outside air temperature sensor connected to a controller. The value of the outside air temperature in that controller can be transmitted across the I/NET network to be used in algorithms in the other controllers.
The I/NET software and firmware provides the mechanism to transmit and receive point data system wide. The outside air temperature point in this example would be called a "global point." The receiving points within the other controllers that reference and thereby mimic the global point's temperature value are called "indirect points."
Resolution
Each controller is capable of a total of 128 global and indirect points. Global points are used to s...