I/NET Global and Indirect Points Overview and Recommendations

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Global and Indirect Points Overview and Recommendations
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3027 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Global and Indirect Points Overview and Recommendations

Picard Product_Support
‎2018-09-10 12:42 AM

Issue

Some issues which this article covers are:

  • What rules or recommendations should be used with Indirect and Global Points?
  • Why might a global point not change?
  • Attempting to alter a global AO/DO points' value/state, by "Point Control" without "Manual Mode" being used, and the change does not take place. (Referred to as Global Output Retentive Feedback.)
  • What scan rates should be used for global / indirect points?

Product Line

TAC INET

Environment

I/NET Software

Cause

Often within a system, a point's status or value within one controller has to be shared or used in other controllers connected to the system. An example could be an outside air temperature sensor connected to a controller. The value of the outside air temperature in that controller can be transmitted across the I/NET network to be used in algorithms in the other controllers.

The I/NET software and firmware provides the mechanism to transmit and receive point data system wide. The outside air temperature point in this example would be called a "global point." The receiving points within the other controllers that reference and thereby mimic the global point's temperature value are called "indirect points."

Resolution

Each controller is capable of a total of 128 global and indirect points.

Global points are used to share information from one controller to another. If a point is not a global point, the state or value of that point is available only to other points in the same controller. If a point is specified as global, you may use it to control an indirect point in another controller. Any internal or external point may be designated as a global point.

When a point is defined as global, a corresponding indirect point must be set up in the additional controller(s) to receive the global point's data. The global point must be designated with the appropriate globalisation level.

There are four (4) different levels of globalisation, as shown below:

  • Local: This point provides information only to this controller. A global setting of "Local" indicates that this point is not a global point.
  • LAN: This point may provide information to an indirect point in any device connected to this controller LAN.
  • Link: This point may provide information to an indirect point in any device connected to this controller's Host LAN. This setting WILL NOT send global data across links headed by NetPlus Routers.
  • System: This point may provide information to an indirect point in any device connected to the I/NET system including ETHERNET. This setting WILL send global data across links headed by NetPlus Routers.

Global points "broadcast" or send their state/value to corresponding indirect points. The frequency of the broadcast depends on the point type.

All global point types broadcast under the following conditions:

  • The controller has been restarted, either by a power restore, the controller's red reset button has been pushed or the database, DCU0000.sav file, has been "Restored."
  • A global point has been changed from "Automatic" to "Manual" or from "Manual" to "Automatic." This does not apply to the Test Mode.
  • A global point changing to or recovering from the "old data" state due to either a communications failure, or an analogue input point falling outside or re-entering its sensor limits (defined within the 'Resident Points' editor).
  • Global analogue points (AI, AO, GI, GO) broadcast whenever their value changes through a range greater than the specified "Broadcast change counts" parameter (defined within the 'Resident Points' editor).
  • Global discrete points (DI, DA, DO, DM, DC) broadcast whenever their state changes.
  • Global pulsed input points (PI) broadcast whenever their "Scans between broadcasts" parameter is exceeded (defined within the 'Resident Points' editor).
  • When requested to by the associated indirect point.

Indirect points "receive" their state/value from their corresponding global points. Indirect points must reside in a different controller from the global point, and they act as receptors for the value or status information broadcast from the global point.

When entering an indirect point, you must specify the name or address of the associated global point. The frequency of the update from the global points depends on the following.

  • Their associated global point broadcasting its status or value.
  • In addition, an indirect point can request an update, at the indirect points scan rate, from their associated global point. This happens when:
    • The indirect point is first entered.
    • When the indirect point's controller is restored or reset (power restore, station restore or the red reset button is pressed).
    • Whenever the local control LAN reconfigures.
    • Whenever an AO or DO indirect point is put into "Manual Mode" or back into "Automatic Mode."
    • When the indirect point has not seen a status/value change from its associated global point within 2 times the indirect point's scan interval it request an update from its associated global point. It then reports the update on its third scan interval. If the indirect point is unable to be updated from its global point (i.e. no communications) then the indirect point will report its last valid updated value/state and will flag the value/state as "Old Data."

Direction of Point Data's Flow

INPUT POINTS

  • (AI, GI, DI and DA): The data flow is from the global input point broadcasting to the associated indirect point only. The flow is "one way" only, that is to say, if the associated indirect point should alter the state or value is not broadcast to their corresponding global point.
    GLOBAL INPUT --------------> LAN -------------> INDIRECT INPUT

OUTPUT POINTS

  • (AO, GO and DO): All output points (both global and indirect) broadcast their state or value changes to the other associated point(s). The flow is "two way," that is to say, a change to either the global or the associated indirect point will change their opposing point's value accordingly.
    GLOBAL OUTPUT <--------------> LAN <----------------> INDIRECT OUTPUT

Click Here to view some recommendations / rules for Global and Indirect Points as well to view this complete article as one document.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (2)
  • Find more articles tagged with:
  • 5487
  • RobertAndriolo24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore