I/A Series G3 BACnet Server (Export) Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series G3 BACnet Server (Export) Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2205 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series G3 BACnet Server (Export) Operation

Picard Product_Support
‎2018-09-07 07:11 AM

Issue

I/A Series G3 BACnet Server (Export) Operation

Environment

I/A Series G3

Cause

Integration to I/A Series G3 from a 3rd party BACnet system

Resolution

If the I/A Series host (ENS or ENC) is licensed as a BACnet server, you can export any number of selected types of objects in the station (regardless of location) to appear as BACnet objects. As such, these objects can service client requests from any networked BACnet devices. Exporting of Niagara schedules and calendars is included. Histories can be exported also, where they appear externally as BACnet Trend Log objects. 

The following I/A Series G3 objects can be exported as BACnet objects (extracted from the Niagara Ax BACnet Guide). 

 

You use the Bacnet Export Manager to export Niagara objects for BACnet. To access the Bacnet Export Manager, go to 'BacnetNetwork' > 'Local Device' and double click on the 'Export Table' under the Local Device. 

You can find details on using the Bacnet Export Manager on pages 4-57 to 4-71 of the Niagara Ax BACnet Guide. The Niagara Ax BACnet Guide is installed with G3 and can be found in \niagara\niagara-3.x.xx\docs.

 

can be exported also, where they appear externally as BACnet Trend Log objects.
from any networked BACnet devices. Exporting of Niagara schedules and calendars is included. Histories
can be exported also, where they appear externally as BACnet Trend Log objects.
(regardless of location) to appear as BACnet objects. As such, these objects can service client requests
from any networked BACnet devices. Exporting of Niagara schedules and calendars is included. Histories
can be exported also, where they appear externally as BACnet Trend Log objects.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 14244
  • bacnetip
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore