How to launch Personnel Manager without using Continuum Explorer?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to launch Personnel Manager without using Continuum Explorer?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Nava
    Nava
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher
  • JohnBoehmer
    JohnBoehmer
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1868 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to launch Personnel Manager without using Continuum Explorer?

Picard Product_Support
‎2018-09-06 02:41 PM

Issue

Can the Personnel Manager be launched without using Continuum Explorer?

Environment

Continuum CyberStation

Cause

Require quick launch.

Resolution

Opening Personnel Manager without opening an existing personnel record.

Create a button in the graphic to launch Personnel Manager.
Edit the button in the Object Properties
Action: Start Windows Program
Windows Program: C:\Program Files\Continuum\Launch.exe
Command Line Arguments: -C –SPersonnel –Offline “-FRoot”

If you want to include a Owner folder location use the following arguments

Command Line Arguments: -C –SPersonnel –Offline “-FRoot” “-Proot\FolderName”

Result: This will launch Personnel Manager from the button on the graphic with no cardholder information configured.

 

Create a graphic and set it up to launch for the user upon login

Create a button in the graphic to launch Personnel Manager.
Edit the button in the Object Properties
Action: Open object
Object: Select a default cardholder to bring up in Personnel Manager

Result: This will launch Personnel Manager from the button on the graphic to the cardholder selected.

 

Create a graphic button from the main menu that launches Personnel Manager to a specific cardholder

If you have made any modification to the Main Continuum menu. Make a copy of the file before editing.
i.e. the default is c:\program files\continuum\userprofile\continuum.mnu

  1. Right click the main page.
  2. Create a new hot spot or edit the Personnel hot spot according to instructions in the
  3. Configuration manual on Menu Pages.

C:\Program Files\Continuum\Launch.exe
-O -SPersonnel "-N\Cardholders\Test_Card" (Note:Cardholders is a folder)

Result: Personnel Manager will open to that card

 

Launch the command line and use the Show command
This is similar to option 2 except the button config is different

In the Personnel button change the parameters to

C:\Program Files\Continuum>cmdline

Result:
This will launch the Command line
Type in Show Test_Card (some cardholder the user knows exists)

Ex. R> show test_card

Personnel Manager will open to that card

 

Change the Continuum Menu Personnel button that launches a listview to select a cardholder
This is similar to option 2 except the button config is different

  1. Create a listview called Launch_PM
  2. In the listview place the following qualifier.

(Name is like Prompt("Name is like", "*"))

For the Personnel button configure the command and arguments lines to be:

C:\Program Files\Continuum\Launch.exe
-O -Slistview "-N\Launch_PM"

Result: This will run the listview, the user can then type in the name of the personnel they know exists after the "*".
The listview will find the user and then they can double click on the user in the listview to bring up Personnel Manager.
 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3307
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore