Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to get the modbus registers from a ICP7188

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to get the modbus registers from a ICP7188
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1431 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to get the modbus registers from a ICP7188

Picard Product_Support
‎2018-09-11 04:00 AM

Issue

  • How do you get the Modbus register list and communication values from a ICP7188 (SP7040) project.
  • Have extracted files from ICP7188 (blue turtle) want to upgrade this to a Xenta 731 or 913, how can I read the current register configuration from this device.

Environment

ICP 7188

Cause

Want to replace a ICP7188 "blue turtle" device with a Xenta 731 or 913 and need to now what the current Modbus configuration / registers are in the ICP7188 device.

Resolution

To retrieve the Modbus values from the ICP7188 (SP7040) project you will need two text files Cfg9100.txt and MAP9000.txt. from the original project. and the following files contained in this ZIP file SP7040.

Note:  If you need to extract these files you can follow the instructions in the "ILink Commissioning Guide" PDF which is contained within the above ZIP file.  If you don't have the LinkTerm application detailed in this document you can download and install it from here.
N.B: After extracting this LinkTerm.zip file there are two files with the extension '.rename', ISDEL and SETUP.  Both these extension must be renamed to '.EXE' and then you can follow the instructions is the above mentioned guide.

After extracting the SP7040 ZIP file to a drive on your PC along with the two text files into the directory proceed with the following steps:

1. Open the TGT9100.xls file. Make sure you have Macros enabled in Excel.

2. Then select the Device Editor button.

 

3. This will move you to the System Device summary with a message indicating there is a mismatch of the configuration files.

Select Yes too load the configuration files

 

This will populate the Table from the txt files copied earlier.

4. Now you can select the + button next to the Type heading

5. Then select the + button next to the Type heading to show the Modbus values for that device.

 

6. To view the communication setup select the + button next to the System heading as seen in the step 4 image.

Labels (2)
Labels:
  • TAC INET
  • TAC Vista
Attachments
SP7040.zip
Linkterm.zip
Tags (1)
  • Find more articles tagged with:
  • 13513
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore