How to disable a Door Alarm with a Key Switch.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to disable a Door Alarm with a Key Switch.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2533 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to disable a Door Alarm with a Key Switch.

Picard Product_Support
‎2018-09-10 06:37 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-12 12:33 AM

Issue

Need an example on how to program a required action where a Door Switch activation triggers alarm sounder to turn on and stay on until a Key Switch is closed.

Product Line

EcoStruxure Security Expert

Environment

Security Expert

Cause

Require a programming example.

Resolution

There may be a number of ways of doing this, one solution is to have a Door Switch trigger an alarm in the Door's Area which triggers an Alarm Output to turn on. A Key Switch Input is linked to another Automation Area that will disarm the Door's Area which turns off the Alarm Output.

 

In this example we will use the following objects:

  • Input        Door_Switch_Input
  • Input        Key_Switch_Input
  • Output        v_Alarm_Output        (a virtual output for this test)
  • Area        Door_Opened_Area
  • Area        Area_Automation
  • Input Type        KeySwitch_InputType

 

Setup

1. Create an Output, in my example this is virtual output v_Alarm_Output.

SX_DoorAlarmKeySwitch_Output.png

2. If not already created create the Area your Door is located, in my example I created Door_Opened_Area.

 

3. On the CONFIGURATION tab set the alarm timings to 0.

SX_DoorAlarmKeySwitch_Area_1.png

4. On the OUTPUTS tab set the Alarm Memory Output to your alarm output.

SX_DoorAlarmKeySwitch_Area_1_AlarmMemory_OP.png

5. create the Area that will be used as an automation area to reset the door alarm. In my example I created Area_Automation for this purpose.

 

6. On the CONFIGURATION tab set the alarm timings to 0.

SX_DoorAlarmKeySwitch_Area_2.png

7. Create a new Input Type, in my example this is KeySwitch_InputType. On the GENERAL tab set the Control Area to the area with your door switch in it. (Door_Opened_Area)

SX_DoorAlarmKeySwitch_InputType_ControlArea.png

8. On the OPTIONS (1) tab, under MISCELLANEOUS OPTIONS, set the Disarm Control Area On Input Restore and Arm Control Area On Input Alarm options.

SX_DoorAlarmKeySwitch_InputType_Options2.png

9. If not already created, create your door switch input. In my example this is Door_Switch_Input.

 

10. On the AREAS AND INPUT TYPES tab set the Area to your door area and the Input Type to Instant.

SX_DoorAlarmKeySwitch_DoorSwitch.png

11. If not already created, create your key switch input. In my example this is Key_Switch_Input.

 

12. On the AREAS AND INPUT TYPES tab set the Area to your automation area and the Input Type to the input type you created earlier (KeySwitch_InputType).

SX_DoorAlarmKeySwitch_KeySwitch.png

13. Go to a Status Page view with these two Areas listed and disarm then arm each of them. This needs to be done after any change to the Area or objects within it (such as inputs) so they will function properly with the new changes.

 

Notes:

  • KeySwitch = Closed -> Alarm disarmed (Area_Automation)
  • KeySwitch = Open -> Alarm armed (Area_Automation)
  • To disable alarm and reset area, KeySwitch must be Closed and then Opened.
  • DoorSwitch needs to be closed for Alarm to be re-enabled with KeySwitch.

 

Usage

1. Armed normal state.

SX_DoorAlarmKeySwitch_StatusPage_NormalArmed.png

2. Door Alarmed.

  • Door_Switch opens triggering alarm in Door_Opened_Area triggering v_Alarm_Output to turn On.

SX_DoorAlarmKeySwitch_StatusPage_Alarmed.png

3. Alarm silenced by Key_Switch.

  • Key_Switch is Closed triggering Door_Opened_Area to be disarmed and v_Alarm_Output to turn Off .
  • Key_Switch is Opened triggering Door_Opened_Area to re-arm.

SX_DoorAlarmKeySwitch_StatusPage_AlarmRestored.png

4. Alarm will not re-trigger again until Door_Switch is closed and Area re-armed.

SX_DoorAlarmKeySwitch_StatusPage_Alarmed_DoorOpen_AlarmReset.png

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • 19947
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.