Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How to create a Binary Input or Digital Input on a MPM controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to create a Binary Input or Digital Input on a MPM controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MaximeLaudren
    MaximeLaudren
  • sesa139513
    sesa139513
  • SaidSawan
    SaidSawan
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1929 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to create a Binary Input or Digital Input on a MPM controller

Picard Product_Support
‎2018-09-06 09:49 AM

Last Updated: Lieutenant MaximeLaudren Lieutenant ‎2022-08-18 09:33 AM

Issue

How to create a Binary Input or Digital Input on a MPM controller

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager (MPM)

Cause

When a Binary Input is created, the object does not work.

There is no documentation on how to create a Binary Input

Resolution

In order to use a Binary Input, both the BI object and the corresponding Analog Input AI object must be added from the object list. For example, if you need to use BI3 with a dry contact, you will also need to add AI3 and toggle its "input type" to Ohms, then save the object. You also need to keep the object in the object list.

With regards to “Input type” for the Binary Inputs: (the "input type" property is in the AI object)

-When set in Volts, anything >= 2VDC will be considered a 1 status.
                                   anything < 2VDC will be conspired a 0 status.

-When set in Ohms, anything < 10kOhm will be considered a 1 status.
                                     anything >= 10KOhm will be considered a 0 status.

Note: When "Input type" is set to ohms, a dry contact must be used for the BI to work properly. BO1 and BO2 of the MPM can be used for example, but not the relays of the TE2 as they are not dry contacts by design.

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (6)
  • Find more articles tagged with:
  • 15152
  • analogue
  • MaximeLaudren22
  • mpm-gw
  • mpm-un
  • mpm-va
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of