User can’t configure floating application on SE7300C
EcoStruxure Building Expert
  SE7000
Can be a bad connection and misconfiguration of parameters
2 PIPES APPLICATION
4 PIPES APPLICATION
NB: Respecting mandatory configuration steps in the diagrams above will improve the solution.
Change over sensor shall be 10K type II thermistor. When water temperature goes below
74°F the system will be in cooling mode and when water temperature goes over 78°F the system will be in Heating mode.
* From the diagrams, the thermostat closes the common side of the connection.